Fault codeF5
OverVoltage(1) happens due to high AC line voltage or transients, possibly from motor regeneration. The manual lists no action for this code.
- Model
- Rockwell Automation PowerFlex 400 FRN 4.xx
- Display shows
- OverVoltage(1) (F5)
- Type
- Fault code
- Source
- Manual p. 25
What F5 means
OverVoltage(1) p. 25
Common causes
- Monitor the AC line for high voltage or transient conditions. Bus overvoltage can also be caused by motor regeneration. Extend the decel time or install a dynamic brake chopper. p. 25
If F5 is still not resolved
The manual gives no further instruction for this code. Open the code table in the PDF or contact Rockwell Automation service.
This page summarises what the manufacturer’s manual says about F5; each statement links to the page it comes from, and quoted lines are copied word for word. It is not a substitute for the manual or for a qualified installer. ManualLib is not affiliated with Rockwell Automation. Found a mistake? Report an error.