Ground Fault means a ground fault occurred in the cable between the inverter and motor or in the motor itself. The manual's first action is: “It may be disabled by setting P0343=0. Shorted wiring in one or more of the output phases. Motor cable capacitance is too large, resulting in current peaks at the output.”
- Model
- WEG CFW-11
- Display shows
- Ground Fault (F074)
- Type
- Fault code
- Source
- Manual p. 66
What F074 means
Ground Fault p. 66
Common causes
- A ground fault occurred either in the cable between the inverter and the motor or in the motor itself. p. 66
What to do
- It may be disabled by setting P0343=0. Shorted wiring in one or more of the output phases. Motor cable capacitance is too large, resulting in current peaks at the output. p. 66