Fault codeF021
DC Bus Undervoltage means the input voltage is too low, there is a phase loss in the input power supply, or the pre-charge circuit has failed. The manual lists no action for this code.
- Model
- WEG CFW-11
- Display shows
- DC Bus Undervoltage (F021)
- Type
- Fault code
- Source
- Manual p. 65
What F021 means
DC Bus Undervoltage p. 65
Common causes
- The input voltage is too low and the DC bus voltage dropped below the minimum permitted value (monitor the value of Parameter P0004): Ud < 223 V - For a 200-240 V three-phase input voltage Ud < 170 V - For a 200-240 V single-phase input voltage (models CFW11XXXXS2 or CFW11XXXXB2) (P0296=0); Ud < 385 V - For a 380 V input voltage (P0296=1); Ud < 405 V - For a 400-415 V input voltage (P0296=2); Ud < 446 V - For a 440-460 V input voltage (P0296=3); Ud < 487 V - For a 480 V input voltage (P0296=4). p. 65
- Phase loss in the input power supply. p. 65
- Pre-charge circuit failure. p. 65
- Parameter P0296 was set to a value above of the power supply rated voltage. p. 65
If F021 is still not resolved
- contact WEG p. 7 “If needed, please, consult WEG.”