The DVPPF02-SL has detected low voltage and the connection to the PLC host on its right side may be faulty. The manual's first action is: “1. Check whether the connection between the DVPPF02-SL and the PLC host on its right side is normal.”
- Model
- Delta DVPPF02-SL
- Display shows
- Low voltage detection error (F2)
- Type
- Error code
- Source
- Manual p. 9
What F2 means
Low voltage detection error p. 11
What to do
- 1. Check whether the connection between the DVPPF02-SL and the PLC host on its right side is normal. p. 11
- 2. Check whether the power supply to the PLC host on the right side of the DVPPF02-SL is normal. p. 11
Before you service the product, read the safety instructions in the manual p. 3.
If F2 is still not resolved
The manual gives no further instruction for this code. Open the code table in the PDF or contact Delta service.
This page summarises what the manufacturer’s manual says about F2; each statement links to the page it comes from, and quoted lines are copied word for word. It is not a substitute for the manual or for a qualified installer. ManualLib is not affiliated with Delta. Found a mistake? Report an error.