Delta DVPPF02-SL Error F2: Low voltage detection error

Delta DVPPF02-SL PROFIBUS DP Communication Slave Module · taken from the manufacturer’s manual, pages cited

Error codeF2

The DVPPF02-SL has detected low voltage and the connection to the PLC host on its right side may be faulty. The manual's first action is: “1. Check whether the connection between the DVPPF02-SL and the PLC host on its right side is normal.”

Model
Delta DVPPF02-SL
Display shows
Low voltage detection error (F2)
Type
Error code
Source
Manual p. 9

What F2 means

Low voltage detection error p. 11

What to do

  1. 1. Check whether the connection between the DVPPF02-SL and the PLC host on its right side is normal. p. 11
  2. 2. Check whether the power supply to the PLC host on the right side of the DVPPF02-SL is normal. p. 11

Before you service the product, read the safety instructions in the manual p. 3.

If F2 is still not resolved

The manual gives no further instruction for this code. Open the code table in the PDF or contact Delta service.